[Beowulf] Re: HVAC and room cooling...
Leif Nixon
nixon at nsc.liu.se
Tue Feb 3 04:21:24 EST 2004
Jim Lux <James.P.Lux at jpl.nasa.gov> writes:
> YOu need to seriously consider a "failsafe" totally automated shutdown
> (as in chop the power when temperature gets to, say, 40C, in the
> room)... Security might be busy (maybe there was a big problem with
> the chiller plant catching fire or the boiler exploding.. if they're
> directing fire engine traffic, the last thing they're going to be
> thinking about is going over to your machine room and shutting down
> your hardware.
Ah, that reminds me of the bad old days in industry.
The A/C went belly up the night between Friday and Saturday. That
triggered the alarm down at Security, who promptly called the on-duty
ventilation technicians and notified us. Excellent.
Except that the A/C alarm was never reset properly, so when the A/C
failed again Saturday afternoon nobody noticed.
When the temperature reached 35C, the thermal kill switch triggered
automatically. Pity that the electrician had never got around to
actually, like, *wire* it to anything.
We arrived Monday morning to the smell of frying electronics.
Expensive weekend, that.
--
Leif Nixon Systems expert
------------------------------------------------------------
National Supercomputer Centre Linkoping University
------------------------------------------------------------
_______________________________________________
Beowulf mailing list, Beowulf at beowulf.org
To change your subscription (digest mode or unsubscribe) visit http://www.beowulf.org/mailman/listinfo/beowulf
More information about the Beowulf
mailing list