Environment monitoring
Robert G. Brown
rgb at phy.duke.edu
Tue Sep 30 16:05:02 EDT 2003
On 30 Sep 2003, Dean Johnson wrote:
> Bummer about the AC. You might want to go and check your backups and
> backup mechanism with a renewed zeal. Based on past experience you are
> in for an "interesting" near future. While they came back just fine, I
> wouldn't expect them to last very long after experiencing that high of
> temp.
Geeze, I forgot to add one more comment. We had just been talking about
the time required for a server room to "get hot" upon the AC shutting
down. Today was AC filter changing day here. Shut down blower unit
(but not cluster) for about 7 minutes. In a room with at least 30 KW
sustained, roughly 4 meters x 10 meters, ambient temperature rose
perhaps 10F, just barely perceptibly (to maybe 75F) by the time the AC
came back on -- warmer immediately behind a rack, of course.
Lots of air, not that efficient a thermal transfer, lots of thermal
ballast to absorb the heat.
rgb
>
> -Dean
>
> On Tue, 2003-09-30 at 14:15, Mitchel Kagawa wrote:
> > This past Friday night after everyone in the office went home our AC, for
> > our small 64 node cluster, decided to have a compressor problem and stop
> > producing cool air. On Sat I get a phone call saying that one of our users
> > can't access his e-mail (server is also in cluster room). I wasn't able to
> > get to the office until Sunday afternoon and I wasn't able to log into the
> > head node to shut everything down remotely. By the time I was able to get to
> > the cluster all but 20 nodes had shut themselves down because the ambient
> > temperature of the room reached 145 deg. Thankfully all the servers, raid
> > arrays and all but 2 nodes came back up when I hit the power button (after I
> > got the temp back to 68). Our stupid ac doesn't have the communications
> > package that cost an extra $5000 cause my company's too cheap to spring for
> > it and an extra phone line. So I was wondering if anyone used one of those
> > environment monitoring appliances that e-mail you (before stuff starts
> > shutting off) if a temp goes out of a set range or if it detects water, high
> > humidity, or movement in the room? I'm looking at a NetBotz/RackBots here
> > (http://www.netbotz.com/products/rack.html) and was wondering if anyone has
> > any experience with them or if you have any other (inexpensive <$2000)
> > suggestions. Thanks for any help.
> >
> > Mitchel Kagawa
> >
> >
> > _______________________________________________
> > Beowulf mailing list, Beowulf at beowulf.org
> > To change your subscription (digest mode or unsubscribe) visit http://www.beowulf.org/mailman/listinfo/beowulf
>
> _______________________________________________
> Beowulf mailing list, Beowulf at beowulf.org
> To change your subscription (digest mode or unsubscribe) visit http://www.beowulf.org/mailman/listinfo/beowulf
>
Robert G. Brown http://www.phy.duke.edu/~rgb/
Duke University Dept. of Physics, Box 90305
Durham, N.C. 27708-0305
Phone: 1-919-660-2567 Fax: 919-660-2525 email:rgb at phy.duke.edu
_______________________________________________
Beowulf mailing list, Beowulf at beowulf.org
To change your subscription (digest mode or unsubscribe) visit http://www.beowulf.org/mailman/listinfo/beowulf
More information about the Beowulf
mailing list