[Beowulf] Re:UPS system for Linux cluster

David Mathog mathog at caltech.edu
Wed Apr 29 13:35:34 EDT 2009


vlad at geociencias.unam.mx wrote:
 
> I have a linux cluster and need to purchase a UPS system.
> The total expected current consumption will be 240 amps. At 120 V this
> would require a 30 kVA UPS system.
> However, I see that 30 kVA systems have a limitation for the input
> current. For example, this 30 kVA system
> (http://www.provantage.com/tripp-lite-su30k3-3xr5~7TRPL1Q9.htm) allows
> only 90 amps as input
> current. I am a bit confused here, and I need some advice on what UPS
> system I should look for.

Do you really need a UPS for the whole cluster?

In many instances it is good enough to put a UPS on the master node and
just use surge suppressors on the compute nodes.  The up side being that
only a small and relatively inexpensive UPS is required.  The down side
being of course that any power failure will break ongoing calculations.
 However, if your work can be check pointed a power failure will only
wipe out the work since the last check point.  If your power is
reasonably reliable, this is a reasonable way to save a lot of money.
Also, unless you are also buying a generator, a whole cluster UPS will
only buy you limited up time during a power failure, so you may well
lose the calculation  despite the large UPS.

Regards,

David Mathog
mathog at caltech.edu
Manager, Sequence Analysis Facility, Biology Division, Caltech
_______________________________________________
Beowulf mailing list, Beowulf at beowulf.org sponsored by Penguin Computing
To change your subscription (digest mode or unsubscribe) visit http://www.beowulf.org/mailman/listinfo/beowulf

-- 
This message has been scanned for viruses and
dangerous content by MailScanner, and is
believed to be clean.



More information about the Beowulf mailing list