At 01:25 PM 3/20/2007, David Mathog wrote:
> > At 04:20 PM 3/19/2007, David Mathog wrote:
>
>On further consideration, that common ground might be
>a problem.  On the one hand it's effectively running from one
>serial port to another and generally that's ok.  On the other
>hand, if for whatever reason one or more of the grounds is
>a volt or two higher than another one, that could result
>in quite a current running on that signal wire.  This would
>probably be safer:


or use diodes.  e.g. 1n5711 or 1N5401

Given that there is probably an alternate grounding path, you 
probably want two diodes for each UPS (one in each line).

or, get a switch with 5 sets of contacts and use 5 sets of batteries 
(I assume you were using Alkaline 9V batteries?)