[Beowulf] ammonite

Jack Wathey wathey at salk.edu
Mon Oct 4 19:37:15 EDT 2004

On Mon, 4 Oct 2004, Jim Lux wrote:

> At 03:19 PM 10/4/2004 -0700, Jack Wathey wrote:
>> http://jessen.ch/ammonite/
> Very nice.. particularly the efforts you put into the cooling air. The 
> comment about flow against a pressure drop is very sound.
> I realize it's a time thing, but had you considered removing the fans from 
> the power supplies?

The linear flow rate through the whole rack is typically about 120 to 200 
fpm, which is sigificantly less than the linear flow rate through a PS. 
If the PS fan was there *only* to cool the mid-tower box it was meant to 
go into, then removing it would do no harm.  But a PS generates a fair 
amount of heat of its own, so I left the fans.  And as you say, it would 
have taken time.

> What's a rough order of magnitude cost on the blower/VFD?  Does this VFD have 
> a "servo" input that could be used to automatically change blower speed in 
> response to temperature?  (some VFDs have an analog input that can be used to 
> set up a speed = linear function of input voltage, and by cleverly setting 
> the gain and offset, you can do quite nicely)

The blower was about $1300, the Teco inverter about $1000.  The inverter 
has an rs232 interface for computer control, which I don't use at present, 
but hope to some day.  It also has the analog control feature you 

Beowulf mailing list, Beowulf at beowulf.org
To change your subscription (digest mode or unsubscribe) visit http://www.beowulf.org/mailman/listinfo/beowulf

More information about the Beowulf mailing list