Back-UPS garbage? (was: Quick survey -- UPSs on slave nodes?)

Joel Jaeggli joelja at
Thu Feb 13 23:03:14 EST 2003

If you want a more relevant anecdote for clusters, in our machines room,
we have three upses... the new one which replaced an excide 25kva unit is
an MGE COMET 65kva unit, the other two are an apc symmetra 12Kva unit with
a secondary battery cabinet and an apc matrix 5000va with 3 xr battery
packs packs... During the outage scheduled to replace the exide with the
comet, the symmetra and the matrix were disconconnected from mains and
generator power for 109 minutes at 75% and 60% load respectivly, when serv
ice was resumed the symmetra was as 8% battery remaining and the matrix
was at 15%. the means out crictical network services remained up through a
nearly 2 hour outage as per our design spec. together the symmetra and the
matrix have nearly 3000 pounds of lead acid gel-cels which is slightly
larger than your average desktop ups.

On Thu, 13 Feb 2003, Dan Christensen wrote:

> Drew Raines <drew-list-beowulf at> writes:
> > No, I didn't get what I paid for.  I paid for it to keep a
> > low-budget PC up for a minute during an outage so I could either
> > reboot the machine, or let the power come back to life.
> The Back-UPS 650 works great for me.  Keeps an OTS PC and monitor up
> for more than half an hour.
> > The box gave me the impression that said unit would do this for 17
> > minutes.  I got 2-3 seconds.
> This is a silly question, but did you remember to plug the battery in??
> If so, then just exchange them, as they are clearly defective.  Lots
> of people use the Back-UPS line.
> Dan
> _______________________________________________
> Beowulf mailing list, Beowulf at
> To change your subscription (digest mode or unsubscribe) visit

Joel Jaeggli	      Academic User Services   joelja at    
--    PGP Key Fingerprint: 1DE9 8FCA 51FB 4195 B42A 9C32 A30D 121E      --
  In Dr. Johnson's famous dictionary patriotism is defined as the last
  resort of the scoundrel.  With all due respect to an enlightened but
  inferior lexicographer I beg to submit that it is the first.
	   	            -- Ambrose Bierce, "The Devil's Dictionary"

Beowulf mailing list, Beowulf at
To change your subscription (digest mode or unsubscribe) visit

More information about the Beowulf mailing list